Will applying salt around earthing electrodes help to resolve neutral to ground line voltage issues?
E&S Grounding Solutions Nov 14, 2019 0 548
Generally speaking, reducing the resistance of the earthing electrodes (salting them) will not help you with a neutral to ground line voltage issue.
Applying salt around earthing electrodes to help resolve neutral to ground line voltage issues
E&S Grounding Solutions Aug 9, 2017 0 1122
No doubt, you will find a subpanel or backup generator somewhere that has a connection from neutral to earth that should not be there and is allowing normal operating neutral currents to travel back on the protective earthing system.